A concrete sewer pipe 3ft in diameter is laid so it has a drop in elevation of 1.0 ft per 1000ft of length. If sewage (assume the properties are the same as those of water) flows at a depth of 1.5ft in the pipe, what will be the discharge?

Q = 10.6 cubic feet/second