Find rate of heat loss from compressor-rate of entropy


Consider an R-134a compressor on a refrigeration system. If the refrigerant enters as saturated vapor at 200 kPa, 0.03 m3/s and leaves at 700 kPa, the power input to the compressor is 10 kW. The 20°C surroundings experience an entropy increase of 0.008 kW/K. Determine (a) the rate of heat loss from the compressor, (b) the exit temperature of the refrigerant, and (c) the rate of entropy generation.

Request for Solution File

Ask an Expert for Answer!!
Mechanical Engineering: Find rate of heat loss from compressor-rate of entropy
Reference No:- TGS0737775

Expected delivery within 24 Hours