Construct time-current characteristics to show coordination


Power System Protection - Mini Project - First Component Radial System Protection

A distribution feeder is 5 miles long and supplies a total load of 5 MVA. Assume that load density throughout the service area is uniform, and that a lateral is built every ½ mile, supplying a service area as shown below:

689_figure.png

Install a recloser on the main feeder at the midway point.

Implement a fuse saving strategy for the laterals.

Assume the maximum fault current values at the substation and at the end of the main feeder are 8 kA and 3.5 kA, respectively.

1. Specify a suitable relay for the substation breaker, a suitable recloser, and a suitable lateral fuse.

Recommendations:

  • Relayed circuit breaker with GE IAC 53 relay
  • Microprocessor-Controlled Recloser (Cooper)
  • Fuse link (speed = T-link)

The devices above will coordinate well, but feel free to make substitutions if you wish.

2. Construct time-current characteristics to show coordination between the substation breaker, recloser, and the fuse on the last lateral.  Be sure to demonstrate that the fuse saving strategy works.

3. Also, propose a means of implementing "fuse saving" (do not cause a sustained interruption for a temporary fault) on the on the first lateral from the substation.

4. Submit your TCCs and a brief narrative of how the protection coordination works.