Consider the heat exchanger design of example 113 that is a


Consider the heat exchanger design of Example 11.3, that is, a finned-tube, cross-flow heat exchanger with a gas-side overall heat transfer coefficient and area of 100 W/m2 · K and 40 m2, respectively. The water flow rate and inlet temperature remain at 1 kg/s and 35°C. However, a change in operating conditions for the hot gas generator causes the gases to now enter the heat exchanger with a flow rate of 1.5 kg/s and a temperature of 250°C. What is the rate of heat transfer by the exchanger, and what are the gas and water outlet temperatures?