At winter design conditions a house is projected to lose


At winter design conditions, a house is projected to lose heat at a rate of 60,000 Btu/h. The internal heat gain from people, lights, and appliances is estimated to be 6000 Btu/h. If this house is to be heated by electric resistance heaters, decide the required rated power of these heaters in kW to maintain the house at constant temperature.