A single-phase load is supplied through a 35-kv feeder


A single-phase load is supplied through a 35-kV feeder whoseimpedance is 95 + j360 ohm and a 35-kV:2400-V transformer whose equivalent impedance is 0.23 + j 1.27 ohm referred to its low-voltage side. The load is 160kW at 0.89 leading power factor and 2340 V.
a. Compute the voltage at the high-voltage terminals of the transformer.
b. Compute the voltage at the sending end of the feeder.
c. Compute the power and reactive power input at the sending end of the feeder.