A church sanctuary is designed for an occupancy of 300


A church sanctuary is designed for an occupancy of 300 persons. The outside airflow rate is 15 cfm per person. The inside design temperature is 74°F and the outside air design temperature is 89°F. Approximate internal heat gains per occupant are 215 Btu/hr for sensible heat and 135 Btu/hr for latent heat.

a. Determine the sensible cooling load component from ventilation.

b. Determine the sensible cooling load component from occupants.

c. Determine the latent cooling load component from occupants.

d. Determine the total cooling load component from occupants.