1-phase 2-winding transformer is rated 30 kva 36090 v 60 hz


1-phase 2-winding transformer is rated 30 kVA, 360/90 V, 60 Hz. A source connected to the 360-V winding supplies an impedance load connected to the 120-V winding. The load absorbs 15 kVA at 0.8 p.f. lagging when the load voltage is 118 V. Assume that the transformer is ideal and calculate the following:

a. The voltage across the 360-V winding.

b. The load impedance

c. The load impedance referred to the 360-V winding

d. The real and reactive power supplied to the 360-V winding