each pole of a 100kw 250v flet-compound generator


Each pole of a 100kW, 250v flet-compound generator has a shunt field of 2000 turns and a series field of 7 turns. If the total shunt field resistance is 100 ohms, calculate mmf when the machine operates at rated voltage.

A) no load

B) full load

Solution Preview :