Calculate the earth loop impedance minimum fault current


Question 1. An 11 kV motor is fed by cables from a transformer via switchgear, having a phase impedance of 0.3 + j0.3 ohm. The earth return path to the transformer neutral has a resistance of 0.42 ohm. Determine a suitable value of neutral resistance if the voltage rise at the motor in the event of an earth fault at the motor is not to exceed 430 V. Neglect transformer winding resistance.

Question 2. Using TABLE 1, determine the resistance of a conductor and the volt drop per ampere metre at 70°C for a 95 mm2 pvc/swa/pvc copper cable. The temperature coefficient of resistance is 0.004 per °C.

Copper Conductor Size

Resistance/metre of Conductor

(microhms per metre)

Resistance/metre of Steel Armour

(microhms per metre)

6 mm2

3080

4600

10 mm2

1830

3700

16 mm2

1150

3200

25 mm2

727

2400

35 mm2

524

2100

50 mm2

387

1990

70 mm2

268

1400

95 mm2

193

1200

120 mm2

153

1100

150 mm2

124

740

185 mm2

99

680

240 mm2

75

600

300 mm2

60

540

TABLE 1 Resistances of Copper Conductor and Steel Wire Armour for 3-core copper PVC Insulated Cables at 20°C.

Question 3. A load, 100 m from a 415 V Supply Authority point is connected by a 35 mm2 pvc/swa/pvc copper cable. The current rating is 119 A and the volt drop per ampere metre is 1.1 mV. If the load current is 90 A, determine whether the volt drop at the load is within the 17th Edition of the IEE Wiring Regulations 5% limit. Using TABLE 1, calculate the earth loop impedance, minimum fault current (neglect the supply/earth impedance) and select an appropriate fuse for the circuit with reference to B.S. 88 part 2 (see FIGURE 3, Lesson 4 - 4).